I'm getting into CT testing, and am having trouble understanding the value of a knee-point excitation test.
The majority of the tests I've done are on 600V CTs between 500-5000A. The knee point values are usually in the mA range at a couple of hundred volts.
My understanding is the ANSI knee is the stable 45 degree slope just before the saturation of the CT core, correct? And this saturation point is the point at which an increase in the primary current would not produce a reliable increase in secondary current, correct?
So, if in actual operation, the saturation point of the secondary is often tens of amps, at very low voltage, how does my knee-point test result at high voltage and low current relate to this?
Am I to simply take it on face-value that it should match the manufacturers published excitation curve? Because any of the curves I'm finding have excitation values much higher than indicated by testing.
Thanks for any help.
The majority of the tests I've done are on 600V CTs between 500-5000A. The knee point values are usually in the mA range at a couple of hundred volts.
My understanding is the ANSI knee is the stable 45 degree slope just before the saturation of the CT core, correct? And this saturation point is the point at which an increase in the primary current would not produce a reliable increase in secondary current, correct?
So, if in actual operation, the saturation point of the secondary is often tens of amps, at very low voltage, how does my knee-point test result at high voltage and low current relate to this?
Am I to simply take it on face-value that it should match the manufacturers published excitation curve? Because any of the curves I'm finding have excitation values much higher than indicated by testing.
Thanks for any help.