We had a motor that was running fine. Took it out for maintenance. Relay calibrations were performed ONLY AFTER the motor was shutdown. All relays are GE style electromechanical relays.
Upon startup of the motor, it tripped on unbalanced current approx 1 second after start. Motor meggered/bridged fine. Changed unbalance relay and started again - tripped approx 1 second after start.
We meggered CT and relay circuit (with neutral ground lifted) - everything fine.
Checked resistive balance on CT's. Very close. Something like 0.56 ohms, 0.56 ohms, 0.57 ohms.
We performed secondary excitation (saturation) test on the CT's (200:5 ratio). Phases C and B had a knee around 90 volts and required 115-120 volts to produce 2A secondary. Looks normal.
Phase A produced 2A secondary at 4 volts. Looks bad. Took it up to around ~10 volts and 5A, then slowly back to zero, then raised voltage again and same results.
To check for possible influences outside the CT on secondary or primary side we checked the following:
For secondary - Determ'ed B phase and A phase CT secondaries (to ensure there was no problem in the wiring) and repeated saturation test and same results.
For primary Verified that bus grounds were hung only on the line side of the CT's, so no apparent loop path on the primary side (except possibly through motor itself... but that should affect all phases equally...presumably a high impedance path?).
We conclude there is a problem with A phase CT that failed it's saturation test.
We were unable to perform ratio test at the time I left site because the primary side was still taped up and we couldn't access it for testing. The plan was to replace the CT.
So now my questions:
Do you think the failure is shorted turn or residual magnetism on the CT?
If shorted turn, wouldn't it show on the resistance test? Maybe not.
If residual magnetism, why didn't we clear it when we increased to 5A excitation current and back down?
In either case, how can the failure possibly be related to the work done which was relay calibration? Test paddles were installed for testing.
I think that saturation could occur if the CT circuit were interrupted while carrying current, but there is no reason to think that happened... testing didn't begin until after the motor was shutdown.
We will have an opportunity to ratio test the removed CT. Will that tell us enough to distinguish between shorted turn, residual magnetism, or some other problem? Is there anything else we should test on the removed CT?
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
Upon startup of the motor, it tripped on unbalanced current approx 1 second after start. Motor meggered/bridged fine. Changed unbalance relay and started again - tripped approx 1 second after start.
We meggered CT and relay circuit (with neutral ground lifted) - everything fine.
Checked resistive balance on CT's. Very close. Something like 0.56 ohms, 0.56 ohms, 0.57 ohms.
We performed secondary excitation (saturation) test on the CT's (200:5 ratio). Phases C and B had a knee around 90 volts and required 115-120 volts to produce 2A secondary. Looks normal.
Phase A produced 2A secondary at 4 volts. Looks bad. Took it up to around ~10 volts and 5A, then slowly back to zero, then raised voltage again and same results.
To check for possible influences outside the CT on secondary or primary side we checked the following:
For secondary - Determ'ed B phase and A phase CT secondaries (to ensure there was no problem in the wiring) and repeated saturation test and same results.
For primary Verified that bus grounds were hung only on the line side of the CT's, so no apparent loop path on the primary side (except possibly through motor itself... but that should affect all phases equally...presumably a high impedance path?).
We conclude there is a problem with A phase CT that failed it's saturation test.
We were unable to perform ratio test at the time I left site because the primary side was still taped up and we couldn't access it for testing. The plan was to replace the CT.
So now my questions:
Do you think the failure is shorted turn or residual magnetism on the CT?
If shorted turn, wouldn't it show on the resistance test? Maybe not.
If residual magnetism, why didn't we clear it when we increased to 5A excitation current and back down?
In either case, how can the failure possibly be related to the work done which was relay calibration? Test paddles were installed for testing.
I think that saturation could occur if the CT circuit were interrupted while carrying current, but there is no reason to think that happened... testing didn't begin until after the motor was shutdown.
We will have an opportunity to ratio test the removed CT. Will that tell us enough to distinguish between shorted turn, residual magnetism, or some other problem? Is there anything else we should test on the removed CT?
=====================================