Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

CT Ratio Selection

Status
Not open for further replies.

Cerkit

Electrical
Jan 18, 2016
99
Hi,

I am looking at a 22/400kV 600MVA transformer. I am looking at CT sizes for the LV side of the transformer. For full load current the current is 15745A. Is it possible to use a 16000/1 CT or does this ratio of CT not exist?

Thanks
 
Replies continue below

Recommended for you

@Cerkit,
What is that CT for? AFAIK, at that range, you can find bushing CTs for that. If you wanted a CT for metering, a 16,000/5 is fine. If you want to use it for protection, a 22,000/5 would be better.
 
I have worked with 19000/1 CT's for a 660MW generator for protection purposes. But yes, what are the CT's for? If for protection please state what kind of protection.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor