CT ratio 1

Status
Not open for further replies.

144x

Electrical
Mar 15, 2001
123
let's assume that we have a CT with this charactristics
core1 600-300-150/1 5p20 30 VA
core2 300 -150 /1 0.5Fs10 20 VA
the rated current of the line is about 600A.is it possible
to use the measuring core in this situation?
thanks
 
Replies continue below

Recommended for you

Depends what the thermal rating and ambient temperature of the CT is. If this is an IEEE C57.13 transformer (and I'm guessing not based on the ratings), standard rating factors will be 1.0, 1.33, 1.5, 2.0, 3.0, and 4.0 at 30 degrees C. In this instance, the CT is required to have an RF of at least 2.0 and ambient of 30 degrees C or lower to run continuously at 600 A. For your non-C57.13 CT, you will have to check with the nameplate, the build/design standard, or the manufacturer.
 