Hello
We have completed a fault study to identify symmetrical fault levels of 50kA RMS and asymmetrical peak fault levels of 100kA according to IEC60909 using SKM.
CT's proposed by the supplier are 2000A/1A 10P40. This implies CT's will not saturate for the RMS symmetrical fault current (i.e. 10% accuracy up to 80kA).
We want to ensure CT's spec'd do not saturate during the asymmetrical fault. How do we ensure this will not happen as the asymmetrical fault level will be accompanied by a DC offset (ie. RMS will be higher)?