I have a question regarding current transformer saturation during fault conditions as listed in the subject title.
Some background: We have a 3-phase induction motor drawing 500A during full load.
I've chosen some current transformers: 500:5, 5P5, 30VA. (Transformers will not saturate during start-up).
The short circuit currents vary between 900A(SLG)-21kA(DLG).
As you can probably tell, the CT's will saturate during a DLG fault.
My question is:
Assuming that a DLG fault happens, will the saturation caused by the DLG fault be a problem for the relay to trip, or will the saturation in the transformers prevent that?
As far as my understanding goes, the fact that 2/3 of the transformers saturate should still register as a fault, the only exception being a 3-phase fault, because then all CT's would be in saturation and the relay wouldn't register this as a problem. Although I don't know if any differential relay is capable of registering a 3-phase fault.
Can someone help?
I have a question regarding current transformer saturation during fault conditions as listed in the subject title.
Some background: We have a 3-phase induction motor drawing 500A during full load.
I've chosen some current transformers: 500:5, 5P5, 30VA. (Transformers will not saturate during start-up).
The short circuit currents vary between 900A(SLG)-21kA(DLG).
As you can probably tell, the CT's will saturate during a DLG fault.
My question is:
Assuming that a DLG fault happens, will the saturation caused by the DLG fault be a problem for the relay to trip, or will the saturation in the transformers prevent that?
As far as my understanding goes, the fact that 2/3 of the transformers saturate should still register as a fault, the only exception being a 3-phase fault, because then all CT's would be in saturation and the relay wouldn't register this as a problem. Although I don't know if any differential relay is capable of registering a 3-phase fault.
Can someone help?