CT saturation in protection

Status
Not open for further replies.

simatic7

Computer
Jun 24, 2009
29
0
0
AU
which protection is more affected by CT saturation ? Any good literature with explanation ? Which is more sensitive to CT saturation ?
 
Replies continue below

Recommended for you

Any protection that has to work when the CT saturates (i.e. when there is a fault).

The most common problem is with current differential protection. In this case, a small mismatch in the saturation characteristics of the CT's can cause nuisance tripping.

See faq238-1287, under Power System Protection

Alan
----
"It’s always fun to do the impossible." - Walt Disney
 

This GE/Multilin white paper discusses CT saturation for certain applications.

If you check the SEL website ( you will find some additional tech papers on CT performance.

If you're REALLY interested, check J.L. Blackburn's Protective Relaying book for a good discussion of CTs and relays.

If you're REALLY, REALLY interested, Stan Zocholl of SEL has published a book on Current Transformers.
 