dvscrobe14
Electrical
- Feb 1, 2015
- 2
I have noticed in the field two ways of injecting CT secondary test current, when testing the integrity of the entire CT circuit that is connected to a CT, once all the burden elements have been individually tested. One way is to break away the leads at the CT terminal board and connect them to a test set. Then, the open CT would be shorted down and grounded. The other way is to leave the CT circuit intact and "piggyback" the test leads onto the circuit, thus creating a parallel path for test current to flow. Typically, .5A, 1.0A and 1.5A would be pushed on the phases and then going to each of the circuit elements to check that the current magnitudes are reading correctly and are on the correct phases. Also, the neutral current would be checked which would be .86A in this case. A lot of my coworkers say that piggybacking is not a good idea but no one can tell me what would happen if you did it that way.