JezNZ
Electrical
- Jun 17, 2021
- 73
Hi All,
I have a current 11kV private network expansion project wherein my company is performing design & build works.
Separately a consultant has been contracted by the client to perform the Fault Study and develop the Protection Settings. They also produced the concept design for the project.
The concept design identified expansion of an 11kV switchboard. The expectation was that the CTs would be provided 200/1 like-for-like (5P10 15VA)) with the existing switchboard tiers and this was expressed to the OEM and procured as such.
Later, the consultant has identified a concern with the CTs and requested to 1. Confirm the thermal rating of the CTs at >= 180%, 2. Perform a CT adequacy check.
Unfortunately, the CT manufacturer (Indonesian) has declined to either confirm the thermal rating or to supply any datasheet information ostensibly claiming IP and the risk of IP theft from Chinese manufacturers.
I can't perform a CT adequacy check without the secondary winding resistance, but I figured I can directly measure this from the CT, is this really feasible/practical? Are there any precautions I should take with regards to the primary of the CT?
Then following, it possible to undertake testing of the CT to determine the thermal rating? My guess is no...
Thanks
I have a current 11kV private network expansion project wherein my company is performing design & build works.
Separately a consultant has been contracted by the client to perform the Fault Study and develop the Protection Settings. They also produced the concept design for the project.
The concept design identified expansion of an 11kV switchboard. The expectation was that the CTs would be provided 200/1 like-for-like (5P10 15VA)) with the existing switchboard tiers and this was expressed to the OEM and procured as such.
Later, the consultant has identified a concern with the CTs and requested to 1. Confirm the thermal rating of the CTs at >= 180%, 2. Perform a CT adequacy check.
Unfortunately, the CT manufacturer (Indonesian) has declined to either confirm the thermal rating or to supply any datasheet information ostensibly claiming IP and the risk of IP theft from Chinese manufacturers.
I can't perform a CT adequacy check without the secondary winding resistance, but I figured I can directly measure this from the CT, is this really feasible/practical? Are there any precautions I should take with regards to the primary of the CT?
Then following, it possible to undertake testing of the CT to determine the thermal rating? My guess is no...
Thanks