I am working on a project that has two 3750kVA 13.8-4.16kV XFMRs installed. They want to swap out these XFMRs to a 7500kVA XFMR. The 4.16kV current on the new XFMR is 1040A. The main breaker CTs are currently 800/5 for the old 3750kVA XFMRs. I was told that the thermal rating would allow the 800/5 CT to work for the new XFMRs if the CT had a CONTINUOUS THERMAL CURRENT RATING FACTOR of 1.33 or higher. I thought that a CT was only good for the rating I have never heard of a CONTINUOUS THERMAL
CURRENT RATING FACTOR that would allow the CT to operate in a range higher than the 800/5. I was told that a 800/5 CT with a 1.5 TR could operate at 1200/5. Is this true? Please advise. I am going to have the main breaker de-energized on Monday to take the CT nameplate to see if the CT can be used for a higher capacity.
I am working on a project that has two 3750kVA 13.8-4.16kV XFMRs installed. They want to swap out these XFMRs to a 7500kVA XFMR. The 4.16kV current on the new XFMR is 1040A. The main breaker CTs are currently 800/5 for the old 3750kVA XFMRs. I was told that the thermal rating would allow the 800/5 CT to work for the new XFMRs if the CT had a CONTINUOUS THERMAL CURRENT RATING FACTOR of 1.33 or higher. I thought that a CT was only good for the rating I have never heard of a CONTINUOUS THERMAL
CURRENT RATING FACTOR that would allow the CT to operate in a range higher than the 800/5. I was told that a 800/5 CT with a 1.5 TR could operate at 1200/5. Is this true? Please advise. I am going to have the main breaker de-energized on Monday to take the CT nameplate to see if the CT can be used for a higher capacity.