Sn00ze
Electrical
- Jan 16, 2013
- 176
Hello all,
Can anyone suggest any good literature about the CT thermal rating vs accuracy?
Question: if you have a CT with TRF of 2. whe you select CT ratio. Do you HAVE to consider it?
meaning: if you have a nominal current of 300A can you select the tap ratio of 400:5 or do you have to go with 200:5 x 1.5 = 300A (Assuming value of 1.5 TRF from IEEE C57.13) ?
I was given this chart by a metering company : As per the Attached the Accuracy of 0.3 is only guaranteed between nominal to Rating factor. can anyone confirm this?
This would mean that if you do not use the Rating factor, you will always be operating at 0.6 accuracy.
Can anyone suggest any good literature about the CT thermal rating vs accuracy?
Question: if you have a CT with TRF of 2. whe you select CT ratio. Do you HAVE to consider it?
meaning: if you have a nominal current of 300A can you select the tap ratio of 400:5 or do you have to go with 200:5 x 1.5 = 300A (Assuming value of 1.5 TRF from IEEE C57.13) ?
I was given this chart by a metering company : As per the Attached the Accuracy of 0.3 is only guaranteed between nominal to Rating factor. can anyone confirm this?
This would mean that if you do not use the Rating factor, you will always be operating at 0.6 accuracy.