NCTHAI
Electrical
- Nov 26, 2007
- 98
Can experts share their experience pertaiing to CT Wiring? Here is the conditions for substation under advance stage of energization:
1) CBCT (Core Balance Current X'mer) is used for earth fault protection in motor feeders and distribution trasnformer feeders (outgoing). CBCT Ratio 150/1 A, Max fault current is limited to 400 A - Limited by use of NGR installed in
- CBCT class is "Class 1"
Any issue with this? Is it normal? What are the implications? Is it not required to have Px or XPXX class CT?
2) For incomer circuits on PCC (power Control Center) differential relay is provided. Also there is separate CT for earth fault potection - From Neutral of trasnformer. This CT is 5P10 class. Differential CT provided is Class Px.
Is there issue with this? The problem is we are mixing CT for differentil and earth fault. So the questuin is is it aceotable to use different class CT for protectin,
Thanks in advane for you advice.
1) CBCT (Core Balance Current X'mer) is used for earth fault protection in motor feeders and distribution trasnformer feeders (outgoing). CBCT Ratio 150/1 A, Max fault current is limited to 400 A - Limited by use of NGR installed in
- CBCT class is "Class 1"
Any issue with this? Is it normal? What are the implications? Is it not required to have Px or XPXX class CT?
2) For incomer circuits on PCC (power Control Center) differential relay is provided. Also there is separate CT for earth fault potection - From Neutral of trasnformer. This CT is 5P10 class. Differential CT provided is Class Px.
Is there issue with this? The problem is we are mixing CT for differentil and earth fault. So the questuin is is it aceotable to use different class CT for protectin,
Thanks in advane for you advice.