For a power transformer that is protected in the primary with a 230kV breaker and a half CB's and 69kV CB at the secondary as shown on the attached SLD, the differential zone should include the high voltage and low voltage side circuit breakers, by connecting the transformer ANSI device 87T differential relays to current transformers on the LINE side of the 230kV breaker and a half CB’s and on the LOAD side of the GIS 69kV incomer CB. However, I was advised to install the CT's of 87T at the primary of the transformer instead at the line side of the 230kV CB. The feeder between the 230kV Sub and 230kV/69kV transformer is via underground cu/XLPE/AWA/PVC cables at approx. 1.1kM. They keep telling me that the 87L line differential relay at Sub 69kV will line transfer trip between 69kV substation to 230kV Substation via F/O cable to the upstream 87L relay in case there is an internal fault within the transformer.
In my understanding, the line diffential is totally different function with transformer differential and there must be a separate dedicated CT's of 87T at the line side of the 230kV breaker and a half CB. Could you please share your expertise?
For a power transformer that is protected in the primary with a 230kV breaker and a half CB's and 69kV CB at the secondary as shown on the attached SLD, the differential zone should include the high voltage and low voltage side circuit breakers, by connecting the transformer ANSI device 87T differential relays to current transformers on the LINE side of the 230kV breaker and a half CB’s and on the LOAD side of the GIS 69kV incomer CB. However, I was advised to install the CT's of 87T at the primary of the transformer instead at the line side of the 230kV CB. The feeder between the 230kV Sub and 230kV/69kV transformer is via underground cu/XLPE/AWA/PVC cables at approx. 1.1kM. They keep telling me that the 87L line differential relay at Sub 69kV will line transfer trip between 69kV substation to 230kV Substation via F/O cable to the upstream 87L relay in case there is an internal fault within the transformer.
In my understanding, the line diffential is totally different function with transformer differential and there must be a separate dedicated CT's of 87T at the line side of the 230kV breaker and a half CB. Could you please share your expertise?