I am currently sizing a PSV which is situated on the discharge of a heat exchanger. The relieving fluid is cooling medium i.e. 75%potable water/25% MEG. Based on API standards, I have sized a rupture disc to prevent against tube rupture and process gas breakthrough. Therefore,the only credible scenario for sizing the PSV is the thermal expansion case. However, I am unsure of what value I should use for my cubical expansion coefficient for the 75%potable water/25% MEG cooling medium. The calculated gravity is ~5 oAPI and API521 suggests using a coefficient of 0.0004oF-1. However, if the cooling medium is 100% water, API suggests a cubical expansion coefficient of 0.0001oF-1. As this value is directly proportional to the required relief rate, it has a large effect on the outcome. This may mean a larger valve than required will be installed.
As the mixture 75%potable water/25% MEG, can I take a weighted mean for the cubical expansion coefficient i.e. say 0.000175oF-1? Does anyone know a standard which documents cubical expansion coefficients for MEG/water mixtures?
As the mixture 75%potable water/25% MEG, can I take a weighted mean for the cubical expansion coefficient i.e. say 0.000175oF-1? Does anyone know a standard which documents cubical expansion coefficients for MEG/water mixtures?