Motor Description; 4kv, 1250hp, 1800rpm, WP2 outdoor vertical motor, with three leads available externallly.
General Background info / Chronology:
2002-2003 - REPAIRSHOPNAME rewound this motor
2003 – 2006 – stored in warehouse
2006 – Installed into PUMP22 position.
Spring 2011 – Removed from PUMP22 due to bearing fault. Refurbished by REPAIRSHOPNAME. Post refurbishment electrical tests sat, including megger, dc hi-pot to 10KVdc, surge test.
Spring 2011 - Installed into PUMP23 position. Plant Insulation resistance test sat (6 Gig-ohms, PI = 4).
Fall 2011 – Air Filters changed
Review of trends (temperature, vibration) from Spring 2011 until Spring 2012 shows no anomalies
Approx 4/10/12 – To support pump work, motor oil drained, motor determinated, motor moved south of pit on outdoor structure (temporary storage location). Hooked up space heaters. Changed air filters.
Severe rainstorm occurred sometime between 4/10/12 and 4/12/12. This should not be a problem since motor is WP2 and normally outdoors.
4/24/12 - Performed megger. Shows short by megger test. Shows approx 0.4 ohms to ground by Fluke all three phases. Verified motor bottom was warm to touch (space heaters working).
4/24/12 approx 1700 - put cover over motor with additional lights for heat under the cover.
4/25/12 approx 0900 - Verified space heaters drawing approximate correct current - 13.2Amps at 120 volts (gives approx 1600 watts, nameplate states 1800 watts).
4/25/12 - Performed bridge tests phase to ground and phase to phase. Results as follows:
Phase to ground tests:
Lead Black Orange Red Average
Phase to ground resistance 0.306 0.304 0.305
Lead resistance 0.06 0.06 0.06
"Phase-to-ground resistance, corrected for leads" 0.246 0.244 0.245
Phase to phase tests:
Leads B-O O-R R-B Average
Phase to phase resistance 0.413 0.413 0.412
Lead resistance 0.06 0.06 0.06
"Phase-to-phase resistance, corrrected for leads" 0.353 0.353 0.352 0.353
Avg Ratio of corrected phase-to-phase and phase-to-ground = 0.353 / 0.245 = 1.439
Obviously, the motor needs repair shop attention. However, I am curious to explain what can cause this pattern. If ratio of phase-to-phase to phase-to-ground was 2.0 (it’s not), we would suspect a hard ground on the neutral. Could this represent severe uniform moisture-related degradation of insulation resistance on all three phases?
=====================================
(2B)+(2B)' ?
General Background info / Chronology:
2002-2003 - REPAIRSHOPNAME rewound this motor
2003 – 2006 – stored in warehouse
2006 – Installed into PUMP22 position.
Spring 2011 – Removed from PUMP22 due to bearing fault. Refurbished by REPAIRSHOPNAME. Post refurbishment electrical tests sat, including megger, dc hi-pot to 10KVdc, surge test.
Spring 2011 - Installed into PUMP23 position. Plant Insulation resistance test sat (6 Gig-ohms, PI = 4).
Fall 2011 – Air Filters changed
Review of trends (temperature, vibration) from Spring 2011 until Spring 2012 shows no anomalies
Approx 4/10/12 – To support pump work, motor oil drained, motor determinated, motor moved south of pit on outdoor structure (temporary storage location). Hooked up space heaters. Changed air filters.
Severe rainstorm occurred sometime between 4/10/12 and 4/12/12. This should not be a problem since motor is WP2 and normally outdoors.
4/24/12 - Performed megger. Shows short by megger test. Shows approx 0.4 ohms to ground by Fluke all three phases. Verified motor bottom was warm to touch (space heaters working).
4/24/12 approx 1700 - put cover over motor with additional lights for heat under the cover.
4/25/12 approx 0900 - Verified space heaters drawing approximate correct current - 13.2Amps at 120 volts (gives approx 1600 watts, nameplate states 1800 watts).
4/25/12 - Performed bridge tests phase to ground and phase to phase. Results as follows:
Phase to ground tests:
Lead Black Orange Red Average
Phase to ground resistance 0.306 0.304 0.305
Lead resistance 0.06 0.06 0.06
"Phase-to-ground resistance, corrected for leads" 0.246 0.244 0.245
Phase to phase tests:
Leads B-O O-R R-B Average
Phase to phase resistance 0.413 0.413 0.412
Lead resistance 0.06 0.06 0.06
"Phase-to-phase resistance, corrrected for leads" 0.353 0.353 0.352 0.353
Avg Ratio of corrected phase-to-phase and phase-to-ground = 0.353 / 0.245 = 1.439
Obviously, the motor needs repair shop attention. However, I am curious to explain what can cause this pattern. If ratio of phase-to-phase to phase-to-ground was 2.0 (it’s not), we would suspect a hard ground on the neutral. Could this represent severe uniform moisture-related degradation of insulation resistance on all three phases?
=====================================
(2B)+(2B)' ?