JohnMcNutt
Industrial
- Mar 3, 2013
- 111
You guys helped me understand the last one well so here is another I have not seen.
20 kW genset where the data plate says 120/240 single phase only. On looking at the gen head it definitely has 12 leads and they are connected in a 120/240 high leg center tapped delta configuration with load taken off 2 corners and neutral at the midpoint. Just as if it was a 3 phase unit.
I do not want three phase from this unit so I will continue to run it as-is but my curiosity is making me wonder how the currents would divide among the windings of this thing if it was loaded unevenly with 120v loads on one side or the other. Obviously 240v only loads would divide with no problem at all.
Thanks for looking
20 kW genset where the data plate says 120/240 single phase only. On looking at the gen head it definitely has 12 leads and they are connected in a 120/240 high leg center tapped delta configuration with load taken off 2 corners and neutral at the midpoint. Just as if it was a 3 phase unit.
I do not want three phase from this unit so I will continue to run it as-is but my curiosity is making me wonder how the currents would divide among the windings of this thing if it was loaded unevenly with 120v loads on one side or the other. Obviously 240v only loads would divide with no problem at all.