Hi all,
I have a motor rated @ 370 W (1/2 HP), 59 N.m and 59 RPM. I would like it to run at 40 RPM and 25 N.m (=109 W) with the help of a VFD in V/Hz mode. The torque limit is for security reasons. I'd like to know the current in the motor line in order to buy the appropriate motor starters / overload protection (and the Variator)!
I have done some calculations and I would like to share it with you, because I am not quite sure about them. To illustrate my thoughts I have done a little graph =)
Point 1->2 : To account for the speed reduction, we would have to reduce the frequency and the voltage to 68% times the initial values.
Point 2->3 : To account for the torque reduction of 25/59 = 0.43, we would have to reduce current by square_root(0.43) = 0.66. Why ? In my understanding the motor torque varies in square proportion to the input current. If we reduce current by 0.66, we´d additionaly have to reduce the voltage to 66% the value of point 2.
So at the end, we would have reduced the Frequency to 68% and the voltage/frequency ratio to 66%. Since the motor is rated for 440V and 60 Hz, this would mean that the input is :
V=0.68*0.66*440V = 197 V
Freq = 60*0.68 = 41 Hz
I suppose the current would then be (Rated Current)*0.66 = 0.95 A * 0.66 = 0.62 A
Am I doing things right ? If yes, I suppose that if I configure my VFD to
1) Motor rated Voltage = 0.66*440 2) Motor rated speed = 60 Hz 3) Required output speed = 41 Hz
Then I will get 0.62 Amps of current !
I have a motor rated @ 370 W (1/2 HP), 59 N.m and 59 RPM. I would like it to run at 40 RPM and 25 N.m (=109 W) with the help of a VFD in V/Hz mode. The torque limit is for security reasons. I'd like to know the current in the motor line in order to buy the appropriate motor starters / overload protection (and the Variator)!
I have done some calculations and I would like to share it with you, because I am not quite sure about them. To illustrate my thoughts I have done a little graph =)
Point 1->2 : To account for the speed reduction, we would have to reduce the frequency and the voltage to 68% times the initial values.
Point 2->3 : To account for the torque reduction of 25/59 = 0.43, we would have to reduce current by square_root(0.43) = 0.66. Why ? In my understanding the motor torque varies in square proportion to the input current. If we reduce current by 0.66, we´d additionaly have to reduce the voltage to 66% the value of point 2.
So at the end, we would have reduced the Frequency to 68% and the voltage/frequency ratio to 66%. Since the motor is rated for 440V and 60 Hz, this would mean that the input is :
V=0.68*0.66*440V = 197 V
Freq = 60*0.68 = 41 Hz
I suppose the current would then be (Rated Current)*0.66 = 0.95 A * 0.66 = 0.62 A
Am I doing things right ? If yes, I suppose that if I configure my VFD to
1) Motor rated Voltage = 0.66*440 2) Motor rated speed = 60 Hz 3) Required output speed = 41 Hz
Then I will get 0.62 Amps of current !