jpl5085
Electrical
- Jan 16, 2001
- 6
I was trouble-shooting a control panel that had 3 small motor starters in it. Whenever I had two starters energized and brought in the third, the contactor would chatter or drop out all three contactors. The problem turned out to be that the 100VA transformer had a 1 amp KLD-R current limiting secondary fuse. And it did what it was supposed to - it limited the current and thus causing the contactors to drop out or chatter (during the initial inductive inrush). By the way the control voltage is 24VAC therefore the fuse should be around 4-6 amps.
OK now the question ... How does this type of current limiting fuse work? It has three characteristics: Current limiting, Short Circuit, slo-blo. I was just curious on the physical design of the fuse.
OK now the question ... How does this type of current limiting fuse work? It has three characteristics: Current limiting, Short Circuit, slo-blo. I was just curious on the physical design of the fuse.