rockman7892
Electrical
- Apr 7, 2008
- 1,159
I'm reviewing a short circuit study for the system on the attached one-line and find that the 69kV bus as well as several downstream 13.8kV Switchgear lineups are overdutied due to the fact that there is a significant amount of generator contribution on the 69kV bus in addition to the two utility lines. There are varying degrees of overduteid equipment ranging from 105% to 150% depending on location and existing gear ratings.
Worst case results were modeled with all generator units running and downstream switchgear with Tie Breakers normally closed which represents normal operating conditions.
I'm trying to determine what solutions exist outside of having to replace switchgear such as the insertion of CLR's or other current limiting devices. One thought is to put a CLR on the 69kV tie however this likely will only satisfy the 69kV gear (and not for case where all gens may be connected to single bus)but would still leave downstream switchgear overdutied due to NC tie breaker. For each switchgear lineup I'm assuming that a CLR would also need to be provided at each tie breaker along with the one in the 69kv tie.
What about putting CLR's on the 13.2kV side of the generator circuits? Would this likely cause voltage stability issues along with other dynamic stability issues?
Others have also suggested the use of a Triggered Current Limiter (TCL) make by G&W to act similar to a current limiting fuse to limit let through current. I've seen some application papers suggest using these in parallel with a CLR to achieve the benefits of current limiting as well as system continuity. Does anyone have any experience with these or suggest a location where these may provide the most benefit (generator circuits ? )
Worst case results were modeled with all generator units running and downstream switchgear with Tie Breakers normally closed which represents normal operating conditions.
I'm trying to determine what solutions exist outside of having to replace switchgear such as the insertion of CLR's or other current limiting devices. One thought is to put a CLR on the 69kV tie however this likely will only satisfy the 69kV gear (and not for case where all gens may be connected to single bus)but would still leave downstream switchgear overdutied due to NC tie breaker. For each switchgear lineup I'm assuming that a CLR would also need to be provided at each tie breaker along with the one in the 69kv tie.
What about putting CLR's on the 13.2kV side of the generator circuits? Would this likely cause voltage stability issues along with other dynamic stability issues?
Others have also suggested the use of a Triggered Current Limiter (TCL) make by G&W to act similar to a current limiting fuse to limit let through current. I've seen some application papers suggest using these in parallel with a CLR to achieve the benefits of current limiting as well as system continuity. Does anyone have any experience with these or suggest a location where these may provide the most benefit (generator circuits ? )