Andy32821
Industrial
- Aug 24, 2003
- 39
Hi guys,
I have tested fifty 75 kva (480 to 208/120) transformers at the facility I work out for the amount of current returning to the transformer via the grounding electrode conductor.
39 of the transformers had no current on the GEC.
4 transformers had between 0.2 and 0.5 amps on the GEC.
4 transformers had between 0.5 and 1.0 amps on the GEC.
1 transformer had 2.5 amps on the GEC.
1 transformer had 6.0 amps on the GEC.
Is it worth the time to chase down what appears to be fault current on the units with less than one amp?
What is an acceptable fault amperage threshold ?
Is this even a valid preventative maintenance test ?
Thanks,
Andy
I have tested fifty 75 kva (480 to 208/120) transformers at the facility I work out for the amount of current returning to the transformer via the grounding electrode conductor.
39 of the transformers had no current on the GEC.
4 transformers had between 0.2 and 0.5 amps on the GEC.
4 transformers had between 0.5 and 1.0 amps on the GEC.
1 transformer had 2.5 amps on the GEC.
1 transformer had 6.0 amps on the GEC.
Is it worth the time to chase down what appears to be fault current on the units with less than one amp?
What is an acceptable fault amperage threshold ?
Is this even a valid preventative maintenance test ?
Thanks,
Andy