Gauss2k
Electrical
- Feb 27, 2004
- 49
I have a question about current transformers saturation.
Here's the situation. The building has a medium voltage breaker with its protection relays, on the primary side of its main transformer. The current transformers used by the relay have a ratio of 50:5A.
The maximum short-circuit current at this point is about 6kA. If a bolted fault happens, what current will the relay "see"?
I believe that the CTs core will saturate and the relay will see the maximum saturated current (maybe about 1000A (equivalent on the primary side)). Since the instantaneous protection is set at about 500A, there should be no problem with that.
But I have someone who tells me that a CT under heavy saturation could have a secondary current that would "drop", and the relay would then become "blind" to the fault. He doesn't have any source to confirm this...
I agree that if the current really drops under those conditions, it is indeed critical, but I doubt this is possible...
Anyone has ever heard of this CT's secondary current dropping under heavy saturation condition?
Here's the situation. The building has a medium voltage breaker with its protection relays, on the primary side of its main transformer. The current transformers used by the relay have a ratio of 50:5A.
The maximum short-circuit current at this point is about 6kA. If a bolted fault happens, what current will the relay "see"?
I believe that the CTs core will saturate and the relay will see the maximum saturated current (maybe about 1000A (equivalent on the primary side)). Since the instantaneous protection is set at about 500A, there should be no problem with that.
But I have someone who tells me that a CT under heavy saturation could have a secondary current that would "drop", and the relay would then become "blind" to the fault. He doesn't have any source to confirm this...
I agree that if the current really drops under those conditions, it is indeed critical, but I doubt this is possible...
Anyone has ever heard of this CT's secondary current dropping under heavy saturation condition?