Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

CUT-IN CUT-OUT PRESSURE FOR FIRE PUMP and JOCKEY PUMP

Status
Not open for further replies.

inkospire

Mechanical
Jan 18, 2013
5
I just need to clear my mind on this...how should I specifically design the cut-in cut-out for both fire pump & jockey pump? Appreciate feedback on this. Thnks.
 
Replies continue below

Recommended for you

Start the fire pump and note the maximum pressure on the discharge gauge. Let's say the pressure is 150 psi. Jockey pump would be set to come on at 140 psi and shut off at 150 psi. Depending on the type of pressure switch, the fire pump would come on at 130-135 psi. NFPA 20 covers the settings. The difference between 130 – 135 PSI would depend on the type of pressure sensing device. The older Mercoid type of devices are difficult to get a five PSI difference. The newer fire pump controllers using a pressure transducer and a PLC on the controller can be set at any pressure.

****************************************
Fire Sprinklers Save Firefighters’ Lives Too!
Interested in “Hands On” Fire Protection Seminars with live fires visit for information.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor