I am checking a calculation where about 160000lb/hr of water from a tank 120°F/60psia drains through around 100' of 6" SCH40 steel pipe and a level control valve to another tank at 1.5psia. The saturation temperature at this pressure is about 116°F so I would expect flashing. The originator recognized this and sized an orifice downstream of the CV to take the last 10psi of pressure drop and prevent flashing in the valve.
My question is, would you consider this to be the best practice or would it be better to go to the valve manufacturer and have them quote a valve with trim to handle the flashing?
Thanks!
My question is, would you consider this to be the best practice or would it be better to go to the valve manufacturer and have them quote a valve with trim to handle the flashing?
Thanks!