Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

D1.1 Visual Inspection

Status
Not open for further replies.

novot

Structural
Mar 25, 2003
7
Are there requirements in D1.1 that require 100% VT on all welds?
 
Replies continue below

Recommended for you

Check out D1.1:12002, 6.9:
"All welds shall be visually inspected and shall be acceptable if the criteria in Table 6.1 are satisfied."
 
We are writing a specification to have a fabricator manufacture a 14 gauge stainless steel (type 316) bracket to support our secondary vault lids. This bracket will require one 3/8” stainless steel hex nut (type 316) welded to the bracket to support damaged URD boxes.
Is there a CSA standard applicable to the above welding? Some articles reference the AWS/AMSE for the welding of the two metals, however I question the referencing since I’m unable to view the documentation.
Should there be precautions adhered to prevent corrosion or fatigue of the metal when welding?
Would be grateful for any specific guidance you may offer.

 