Hi,
One 110 kW inverter fed 400 V motor got damaged, after a couple of weeks of operation , due to insulation failure. The motor was fed through one hundred metres of cable and I presumed the motor winding got stressed due to the successive peak wavefronts -the so called voltage doubling reaction.
However, another motor 100 kW capacity , also inverter-driven, and also fed from about 100 metres of cable is operating well since years-five to six years.
I am requesting my management to install output reactors on both drives but they do not believe this argument as the 100 kW is operating without any problem. I am stuck but
I am convinced that the 100 kW will burn sooner or later.
According to literature, the peak voltage on the terminal of the motor should be around 212 % the DC bus voltage i.e 1260 V which is too much for a 10OO V insulation class motor.
Any suggestion.
Bob
One 110 kW inverter fed 400 V motor got damaged, after a couple of weeks of operation , due to insulation failure. The motor was fed through one hundred metres of cable and I presumed the motor winding got stressed due to the successive peak wavefronts -the so called voltage doubling reaction.
However, another motor 100 kW capacity , also inverter-driven, and also fed from about 100 metres of cable is operating well since years-five to six years.
I am requesting my management to install output reactors on both drives but they do not believe this argument as the 100 kW is operating without any problem. I am stuck but
I am convinced that the 100 kW will burn sooner or later.
According to literature, the peak voltage on the terminal of the motor should be around 212 % the DC bus voltage i.e 1260 V which is too much for a 10OO V insulation class motor.
Any suggestion.
Bob