petronila
Electrical
- Jul 28, 2005
- 491
Hello All,
Some paper that I have readed do not make difference between D.A.R and P.I, we know DAR is the ratio between IR measurements taken after 60 and 30 seconds or R 60/R30 and PI is ratio between IR measurements taken after ten minutes and one minute IR = R10/R1 but result interpretation are different in each test.
IMO the test should be called Dielectric Absorption Test or Time-Resistance Test , and depending of how was performed then re-name like DAR or PI, it this corect?
What do you think about this?
Thanks for your inputs
Regards
Petronila
Some paper that I have readed do not make difference between D.A.R and P.I, we know DAR is the ratio between IR measurements taken after 60 and 30 seconds or R 60/R30 and PI is ratio between IR measurements taken after ten minutes and one minute IR = R10/R1 but result interpretation are different in each test.
IMO the test should be called Dielectric Absorption Test or Time-Resistance Test , and depending of how was performed then re-name like DAR or PI, it this corect?
What do you think about this?
Thanks for your inputs
Regards
Petronila