gsjhand
Electrical
- Jul 17, 2007
- 34
I am working in a mill and have 5HP Powerflex 70 VFD connected to mat former rolls. Drives are running in sensorless vactor mode. Recently I started getting DC bus overvoltage faults on one of the drives. This fault is intermittent. What I have observed is that drive is constantly switching between regen and at speed (which is displayed on its HIM screen) and at same time dc bus voltage varies from 810 volts to 1000 volts. There is a DB resistor connected to the drive. According to my understanding all the energy from regen should go to the DB resistor but in this case this dosen’t seems to be happening quickly enough and I am thinking that this might be causing DC bus voltage to rise above limits. Does this mean that DB resistor is too small? Is there any calculation by which I can calculate required value of DB resistor? Supply voltage is 600 Volts 60 Hz. DB resistor connected to drive has rating 0-1000 V DC (PWM); 120 ohms, 260 watts
I would greatly appreciate any help provided in his regard
Thanks