-
1
- #1
Ryc92
Electrical
- May 15, 2011
- 10
Hi there,
We have a 250V DC UPS system here (CCGT power station), fed by two strings of batteries (125V DC string, 250V across both) and three battery chargers (two dedicated to each string, one with a changeover switch to charge either string).
On the charger for one of the strings (and also the other charger when switched to this string) is alarming for an earth fault on the DC side. This is an ungrounded system, with earth fault protection in the form of an insulation resistance monitoring device (set between 5 and 200Kohm). With the protection relay wound up to max (200Kohm) the alarm still stands.
Unfortunately, we cannot simply turn off this system for obvious reasons, and I am looking for a method for locating this fault on load (if possible). When voltage testing to earth, we also get funny voltages (such as 53V to earth on one side, say minus 160V on the negative side). We still get the 125V across the string, and the polarity is correct (we still get 250V across both). We cannot explain why we get these strange floating voltages to earth.
Any help would be greatly appreciated!
Many thanks, Ryan
We have a 250V DC UPS system here (CCGT power station), fed by two strings of batteries (125V DC string, 250V across both) and three battery chargers (two dedicated to each string, one with a changeover switch to charge either string).
On the charger for one of the strings (and also the other charger when switched to this string) is alarming for an earth fault on the DC side. This is an ungrounded system, with earth fault protection in the form of an insulation resistance monitoring device (set between 5 and 200Kohm). With the protection relay wound up to max (200Kohm) the alarm still stands.
Unfortunately, we cannot simply turn off this system for obvious reasons, and I am looking for a method for locating this fault on load (if possible). When voltage testing to earth, we also get funny voltages (such as 53V to earth on one side, say minus 160V on the negative side). We still get the 125V across the string, and the polarity is correct (we still get 250V across both). We cannot explain why we get these strange floating voltages to earth.
Any help would be greatly appreciated!
Many thanks, Ryan