Thanks all, My question, as banal as it might seem, involves the rating on DC breakers. while installing a 48 volt battery bank and its attendant inverter (magnum MS 4448PAE) i have come across an interesting problem, short of the items offered by the major players in the market, nobody seems to offer a dc circuit breaker that is rated for a 48 volt battery banks. Lots of 24 VDC and 150 VDC (PV types) but nobody offers a simple single circuit breaker for the 48 volt range. I am not looking for a din rail type as the system involves only one inverter and a battery bank no solar, nothing other than a 110 VAC line in to maintain the battery banks when not in use. (Simple UPS for a fridge/freezer in a cabin for the odd time when power goes out for a day or so.)
All off the easily available (to me) individual circuit breakers are rated at 12, or 24 volts. examples given: 24 volts 200 amps, 12 volts, 300 amps. My question is can these be used in a 48 volt system (DC) and if so does this derate the breaker in some fashion? these are all the simple heat and break type that heats up and then releases the circuit when x temperature is achieved over x seconds. which can then be manually reset.
It would seem in my non electrician mind, that as the voltage rises in the circuit the amount of amperage that it could handle would correspondingly drop. (battery banks keep the amperage the same as you series wire them for more voltage so it would seem that conversely a fuse or circuit breaker that is rated as 12 or 24 volts the amount of amperage that it could handle would drop if you raised it to 48 volts. IE: a 24VDC breaker rated at 400 amps could only carry 200 amps at 48VDC. a 12 VDC breaker rated at 400 amps could only carry 100 amps at 48VDC.
I was looking at carrying the full load of the inverter at the makers (magnums) recommended over current device rating of 175 amps
"NEC Current is based on the Maximum Continuous Current rating with a 125% NEC derating for sizing the overcurrent device (when not continuous duty) to prevent operation at more than 80% of rating.": from their manual.
However nobody sells on ebay or amazon (my only choices due to location) a 48 volt circuit breaker (or fuse for that matter) in that range that is not a Din rail setup which requires an additional 2~300 dollars worth of unnecessary items. Only 200 or 300 slow blow fuses that are designed to blow over 40 or 50 seconds at their rated (200 or 300) amps. what would happen if I used a 24 VDC 300 or 400 amp circuit breaker in its stead?
thoughts? sage advice? screaming fits about these morons on the interwebz?
thanks
Ken Morgan
All off the easily available (to me) individual circuit breakers are rated at 12, or 24 volts. examples given: 24 volts 200 amps, 12 volts, 300 amps. My question is can these be used in a 48 volt system (DC) and if so does this derate the breaker in some fashion? these are all the simple heat and break type that heats up and then releases the circuit when x temperature is achieved over x seconds. which can then be manually reset.
It would seem in my non electrician mind, that as the voltage rises in the circuit the amount of amperage that it could handle would correspondingly drop. (battery banks keep the amperage the same as you series wire them for more voltage so it would seem that conversely a fuse or circuit breaker that is rated as 12 or 24 volts the amount of amperage that it could handle would drop if you raised it to 48 volts. IE: a 24VDC breaker rated at 400 amps could only carry 200 amps at 48VDC. a 12 VDC breaker rated at 400 amps could only carry 100 amps at 48VDC.
I was looking at carrying the full load of the inverter at the makers (magnums) recommended over current device rating of 175 amps
"NEC Current is based on the Maximum Continuous Current rating with a 125% NEC derating for sizing the overcurrent device (when not continuous duty) to prevent operation at more than 80% of rating.": from their manual.
However nobody sells on ebay or amazon (my only choices due to location) a 48 volt circuit breaker (or fuse for that matter) in that range that is not a Din rail setup which requires an additional 2~300 dollars worth of unnecessary items. Only 200 or 300 slow blow fuses that are designed to blow over 40 or 50 seconds at their rated (200 or 300) amps. what would happen if I used a 24 VDC 300 or 400 amp circuit breaker in its stead?
thoughts? sage advice? screaming fits about these morons on the interwebz?
thanks
Ken Morgan