I'm working on a winching/hoisting application. The load in question is being raised/lowered by a spool, driven by a DC motor. I expect the motor is a simple series wound DC drive, but I don't have one here at the desk to be certain. I do know that the motor is not a permenant magnet, or three pole (only has two brushes).
My problem is in the control circuitry for this drive. The winch operates on 110v DC, and uses a reversing switch for direction control. When the control pendent is in neutral/off, the winch poles are shorted, and the power poles are open. Pressing extend or retract performs as expected.
I can't see any filtering/suppresion devices on the circuit; by meter or eye.
Using two DPDT relays, we attempted to build a magnetic reversing switch (so we could operate with 12v signal). The winch circuit breaker is rated a 7 amp. My first contactor choice was for a 20amp relay (as they were common here). We found after about seven activations the contacts would fuse. My expectation was simply a case of surge current from a "bumping" of the controls.
We stepped up the size of the relays, and exchanged them for solid state type going on the advice from a vendor. The new 50amp solid state relays are able to handle the switching; but are a bit expensive.
It has come time to design another control circuit for a similar application. Instead of forging on with the SSR's and high cost, I wanted to see if I could find the source of the arcing contacts.
Could the contact spacing on the relays just have been too small, causing the arc? Could the arc have been caused by the EMF of the motor start/stop rapidly combined with the motor being driven by the load (these units do not have any dynamic braking). Is there a combination of cap/resistor I should be using to help prevent the arcing? How do I then calculate the cap/resistor value?
Thanks for any help;
Chris
My problem is in the control circuitry for this drive. The winch operates on 110v DC, and uses a reversing switch for direction control. When the control pendent is in neutral/off, the winch poles are shorted, and the power poles are open. Pressing extend or retract performs as expected.
I can't see any filtering/suppresion devices on the circuit; by meter or eye.
Using two DPDT relays, we attempted to build a magnetic reversing switch (so we could operate with 12v signal). The winch circuit breaker is rated a 7 amp. My first contactor choice was for a 20amp relay (as they were common here). We found after about seven activations the contacts would fuse. My expectation was simply a case of surge current from a "bumping" of the controls.
We stepped up the size of the relays, and exchanged them for solid state type going on the advice from a vendor. The new 50amp solid state relays are able to handle the switching; but are a bit expensive.
It has come time to design another control circuit for a similar application. Instead of forging on with the SSR's and high cost, I wanted to see if I could find the source of the arcing contacts.
Could the contact spacing on the relays just have been too small, causing the arc? Could the arc have been caused by the EMF of the motor start/stop rapidly combined with the motor being driven by the load (these units do not have any dynamic braking). Is there a combination of cap/resistor I should be using to help prevent the arcing? How do I then calculate the cap/resistor value?
Thanks for any help;
Chris