Hi all, I have an older 200 HP Reliance RPM DC motor (stab. shunt) with a dual voltage field (300/150 Volt). The armature is 500 volt & 320 amp. The speed is 1150/1750 RPM (constant torque to 1150 w/ blower and constant power from 1150 to 1750). I've measured the resistance of both field windings (F1-F2 and F11-F22) to be 41.3 ohms at room temp.
My question is regarding the nameplate info. on the field which says:
Field volts: 300/*150
Field max. amps: 3.77
Field amps: **
*Sep. Exc. **2.88/1.5-HFA-F1F2F11F22
Based on ohms law before the winding heats up and increases the winding resistance, I get the following:
Using the high voltage connections and applying 300 volts will yeild about 3.6 amps, and using the low voltage connections and applying 150 volts will yield about 7.3 amps.
So how do I interpret the nameplate data
"*Sep. Exc. **2.88/1.5-HFA-F1F2F11F22"?
Does this mean 2.88 amps using the high voltage connections and the windings are at their max. temperature?
Does this mean 1.5 amps using the high voltage connections while the motor is at 1750 RPM?
Why would the low voltage field connection (150 Vdc) exceed the field max. amps nameplate value?
And HFA?
I have a call in to the Rockwell/Reliance support group, but I figure one of you out there surely knows. Any help would be appreciated. Thanks.
My question is regarding the nameplate info. on the field which says:
Field volts: 300/*150
Field max. amps: 3.77
Field amps: **
*Sep. Exc. **2.88/1.5-HFA-F1F2F11F22
Based on ohms law before the winding heats up and increases the winding resistance, I get the following:
Using the high voltage connections and applying 300 volts will yeild about 3.6 amps, and using the low voltage connections and applying 150 volts will yield about 7.3 amps.
So how do I interpret the nameplate data
"*Sep. Exc. **2.88/1.5-HFA-F1F2F11F22"?
Does this mean 2.88 amps using the high voltage connections and the windings are at their max. temperature?
Does this mean 1.5 amps using the high voltage connections while the motor is at 1750 RPM?
Why would the low voltage field connection (150 Vdc) exceed the field max. amps nameplate value?
And HFA?
I have a call in to the Rockwell/Reliance support group, but I figure one of you out there surely knows. Any help would be appreciated. Thanks.