DC motor testing

Status
Not open for further replies.

Wedoca

Electrical
May 5, 2009
70
Question!! I got a DC motor that has quit on me ....I meggered it ...

+ to G is 430M ohms
- to G is 2M ohms
+ to - is 350M ohms

doesn't seems right to me, am I doing it wrong ??? is there a difference on testing AC and DC motors??
 
Replies continue below

Recommended for you

You sure about those numbers? What are the motor ratings? What voltage did you test at? What was your PI? What was winding temp at time of test?
 
Motor infor:

1/4 HP
12VDC
2600RPM
Tested at 250V
I did not do the PI,
the testing enviorment temperture I would say it was about 95 degree F
 
350 MegOhms from + to - looks like an open. Second to roydm, check the brushes.

Bill
--------------------
"Why not the best?"