I'm wondering if all the interlocks i have in P&IDs must be shown in the DCS scrrens.

Thanks in advance.
 
Replies continue below

Recommended for you

If I were the end user, I would want to see them. Having said that I've been away from the process industry too long (in machine design last 15 years) to know what they are presently doing.

David Baird
Sr Controls Designer
EET degree.
 
I wouldn't show them on the DCS main graphics (the ones that may represent your P&IDs). But if a valve or motor is interlocked, the user should be able to open the valve or motor faceplate and determine why it is interlocked from the faceplate (popup window that usually contains the command buttons...open/close...start/stop...).

I recommend a text description of the interlock, not the code, as most users can't read the code.

______________________________________________________________________________
This is normally the space where people post something insightful.
 
Some of DCS have the built-in capability to show its logic on operation screen. Rather than creating the new graphic solely for logic display purposes, it is maybe simpler to just provide the link from the main graphic to this built-in display.
 