Sorry if this is covered already, couldn't find it (likely didn't search correctly) . . .
Our local utility limits pole mount transformers to 300kva, thus 300hp max motor load. Deep well pumps often teeter on the edge of that (i.e. development testing might indicate "325hp max"). The service construction expense of exceeding 300hp (switch to pad mount transformers, more expensive meter mains, etc.) is significant, so users are motivated to understate potential load. Pump company contractors routinely re-stamp new motor nameplates (like, 350hp re-stamped to 300hp) to help users avoid that cost step-up. We understand (and practice when warranted) oversizing motors and controls within reason to improve reliability/longevity, but that practice seems problematic to me when nearing the utility supply limit threshold. Typically only the HP rating is altered, pretty obvious what's going on and would take a lot more effort (like an actual counterfeit nameplate) to hide the true motor rating - but apparently no one looks too closely.
When asked for an opinion I warn that regardless of pump bowl trim & actual load, across-the-line inrush current hinges on actual motor HP and rotor design. I caution that a utility transformer overload failure is likely to generate a big repair bill, and that responsibility for that cost might land on whoever yielded the stamp hammer if the cause is traced back to misrepresentation. We have to date declined(many)requests to do the actual physical restamping.
Now of course most are on soft starts or VFDs so starting currents (and in the case of VFDs full load currents) are adjustable/settable, and in good conscience we have performed those adjustments after the fact to keep everyone out of trouble. Still, if I were a utility engineer I would be thinking any settings turned down can be turned right back up.
What do you guys think? Is it ethical to install a new 350hp motor & VFD, stamp the nameplate and turn in the load on the utility application as 300hp, even though someone could come along later and override our programmed current limits?
Our local utility limits pole mount transformers to 300kva, thus 300hp max motor load. Deep well pumps often teeter on the edge of that (i.e. development testing might indicate "325hp max"). The service construction expense of exceeding 300hp (switch to pad mount transformers, more expensive meter mains, etc.) is significant, so users are motivated to understate potential load. Pump company contractors routinely re-stamp new motor nameplates (like, 350hp re-stamped to 300hp) to help users avoid that cost step-up. We understand (and practice when warranted) oversizing motors and controls within reason to improve reliability/longevity, but that practice seems problematic to me when nearing the utility supply limit threshold. Typically only the HP rating is altered, pretty obvious what's going on and would take a lot more effort (like an actual counterfeit nameplate) to hide the true motor rating - but apparently no one looks too closely.
When asked for an opinion I warn that regardless of pump bowl trim & actual load, across-the-line inrush current hinges on actual motor HP and rotor design. I caution that a utility transformer overload failure is likely to generate a big repair bill, and that responsibility for that cost might land on whoever yielded the stamp hammer if the cause is traced back to misrepresentation. We have to date declined(many)requests to do the actual physical restamping.
Now of course most are on soft starts or VFDs so starting currents (and in the case of VFDs full load currents) are adjustable/settable, and in good conscience we have performed those adjustments after the fact to keep everyone out of trouble. Still, if I were a utility engineer I would be thinking any settings turned down can be turned right back up.
What do you guys think? Is it ethical to install a new 350hp motor & VFD, stamp the nameplate and turn in the load on the utility application as 300hp, even though someone could come along later and override our programmed current limits?