sparky1976
Electrical
- Mar 12, 2001
- 87
All,
I've read the REA Bulletin 1724E-200 about design manual for high voltage trasmission lines. Page 8-2 on 8.2.3 "Deadends : In situations where the insulator string is in line with the conductor , the number of bells should be two more than what was used for tangent structure".
I try to find the reason of that additinal 2 bells for horizontal strings.
In my experince the vertical insulator is more prone to flash over than horizontal because the dirt on horizontal is easier to wash by rain than the vertical string.
Some one told me that for the practical reason, because the work on horizontal string is hard/complicated (its more complicated if you do it hot) than to work on vertical strings, so if one bell damage on horizontal we still can say it still safe.
please advise.
regards
Pitat
I've read the REA Bulletin 1724E-200 about design manual for high voltage trasmission lines. Page 8-2 on 8.2.3 "Deadends : In situations where the insulator string is in line with the conductor , the number of bells should be two more than what was used for tangent structure".
I try to find the reason of that additinal 2 bells for horizontal strings.
In my experince the vertical insulator is more prone to flash over than horizontal because the dirt on horizontal is easier to wash by rain than the vertical string.
Some one told me that for the practical reason, because the work on horizontal string is hard/complicated (its more complicated if you do it hot) than to work on vertical strings, so if one bell damage on horizontal we still can say it still safe.
please advise.
regards
Pitat