Deaerator in Sec.I ?

Status
Not open for further replies.

90harley

Industrial
Mar 9, 2009
34
In the HRSG system will the Deaerator located in the LP section above the LP drum commonly fall under the requirements of Section I ? Or will the boundary end with the LP drum and the DA be considered as an attachment?
 
Replies continue below

Recommended for you

The DA is a pressure vessel in accordance with Section VIII.
Cheers,
gr2vessels
 
it becomes cheaper to built to Sect VIII than I.
 
It really depends on the location and valving. If not isolated outside the ASME I boundary, it will be governed by ASME I. We have seen them designed, manufactured and stamped per ASME I and ASME VIII, Div. 1.

 
Better still, get rid of the DA;- with oxygen controlled injection you have better corrosion control over the whole system and a lot less headaches.
 