In this heavy snow area (100 psf) deck ledgers often fail, and the fasteners (lag bolts, SDS screws) just do not calc out except for the smallest decks. For that reason, I've specified that the deck hangers are to be nailed through the siding (usually T1-11) into the rim joist, with blocking between the joists at that point, so there is no ledger.
The inspector just questioned this method, stating that the Simpson catalog shows hangers fastened directly to a header or other wood member without the intervening siding. He does not feel we would get the full value of the hanger this way.
Any suggestions or comments would be appreciated.
John