I have a 10-ft beam span under uniform loading, supporting visual screens (projection similar to monitors). Deflection is at L/1000 and I want to know if this will be visible to end users at 20~40 ft away. For non building structures without specific deflection limit, what would be typial slpe that will be bsible to others? Thank you.
 
Replies continue below

Recommended for you

Normal limit for visual deflection in buildings is L/250. At L/1000 I would doubt that you could see the deflection from this distance.

Do the screen suppliers give recommended deflection limits?
 
I suggest a very tight deflection spec if the load vibrates.
 
As BUGGAR said, if the load is applied or removed rapidly then you will likely have a more obvious effect than if it was slowly applied and removed.

I'd go for L/800 which is what bridges are limited to in AASHTO.

Professional and Structural Engineer (ME, NH, MA)
American Concrete Industries
 
TehMightyEngineer said:
I'd go for L/800 which is what bridges are limited to in AASHTO
What does a bridge deflection have in common with visual screens?
 
It's a structure subject to rapid loading and unloading that I imagine would scale well to the distance the OP's clients are viewing the monitors and the size of his/her 10 ft beam. Seemed like a good starting point.

Professional and Structural Engineer (ME, NH, MA)
American Concrete Industries
 