Hi guys, I'm new to the forums and hoping to get some advice on a power transformer.
So basically this is a portable machine powered by a 1000v supply having core balance earth leakage on the protection relay and backup earth leakage on the NER. My issue is that part of the machine is powered by a 1000v/415v delta/delta 20kva transformer. The 415 side of circuit has some small 415v dol motors and some control circuitry. My issue is that since the secondary 415v side has no earth reference the equipment supplier is saying to jump the 1000v earth accross and use that for a secondary earth. When testing voltages from the 415 side to primary earth we are getting l1 218v l2 236v l3 264v, these readings are with losd and no load.
So, is the primary earth a suitable reference to detect ground faults on the secondary side.
Thanks in advance,
Sam
So basically this is a portable machine powered by a 1000v supply having core balance earth leakage on the protection relay and backup earth leakage on the NER. My issue is that part of the machine is powered by a 1000v/415v delta/delta 20kva transformer. The 415 side of circuit has some small 415v dol motors and some control circuitry. My issue is that since the secondary 415v side has no earth reference the equipment supplier is saying to jump the 1000v earth accross and use that for a secondary earth. When testing voltages from the 415 side to primary earth we are getting l1 218v l2 236v l3 264v, these readings are with losd and no load.