Delta Secondary-Line to Neutral Relationship

Status
Not open for further replies.

bbleiler

Electrical
May 18, 2003
6
What is the line to neutral mathematical relationship in a delta connected transformer secondary? As in, why is the "wild leg" voltage 208 volts, when the line to line voltage is 240 volts?
 
Replies continue below

Recommended for you

A delta connected secondary of a transformer does not have a neutral connection. Therefore there is no mathmatical relationship. Each of the phases is floating with respect to the neutral. If it where a Y connected, then the phase to neutral voltage would be Voltage Line to line / Square root(2.
 
RickoZone - It is the square root of 3 - not 2, in your formula.
 
The 208 V comes from taking line to line (240 V) and multiplying by the sine of 120 degrees, i.e. the phasor angle between the three phases. My calculator gives 207.85 V as the actual value, rounded easily to 208.
 