In India except in one state,connection used for these sub transmission transformers is YNyn (star/star).Earlier(30years back) we used to provide a stabilising tertiary winding in such transformers.In one state 110kV delta is used as primary.Eventhough they want to switchover to star, parallel operation concerns prevent them. Remember a delta primary with OLTC on primary will be costlier by 10-15 %. Unlike in the star case, the tap changer will be always at 110 kV potential with delta connection, a weak link from maintenance concerns.