DM61850
Electrical
- Sep 9, 2019
- 80
Can you set a REF protection on a transformer that has high impedance resistive ground? I am looking in the manual of the SEL-787 and it looks like it says to not use it if you have a high impedance ground but later it mentioned it can be used on transformers with grounding resistors. Can you use REF but it is just not recommended on high resistive or inductive ground or just not inductive grounding?
This is what the SEL-787 manual says:
"Restricted earth-fault (REF) protection comes from a zero-sequence
directional element that provides sensitive detection of ground faults near the
neutral of a grounded wye-connected transformer winding. The REF element
is intended for resistance and solidly grounded transformer applications. This
element should not be applied to protect high-impedance grounded
transformers."