Delta - Wye Power Transformers

Status
Not open for further replies.

TooFar

Electrical
Jan 14, 2003
1
Could someone please explain why most power transformers in utility substations are Delta - Wye. Is it because of the imbalance on the load side(Wye) of the transformer. Also, is there a 30 degree phase shift across the transformer.
 
Replies continue below

Recommended for you

Delta-wye transformers are useful for a number of reasons. For transmission and distribution lines that are solidy-grounded, the delta-wye provides an excellent ground reference and source of ground current for clearing faults. Also, the delta-wye configuration isolates zero sequence current on each side of the transformer so that ground current relaying on one side does not see ground fault current for a ground fault on the other side.

Yes, there is a phase shift. For an ANSI transformer, the low side will always lag the high side by 30 degrees, regardless of the relative position of the delta and the wye windings.

 