Sea cooling water system provides the main cooling medium for heat removal in to our plant through heat exchangers. The cooler details are as follows.
Fixed tube ASME code, section VIII, Division 1, 1998 Edition and 1999 addenda
Tube material- ASTM B111 C71640
Tube side: seawater / shell side: Natural Gas
Design Temp tube side : 85/-64 °C & shell side : 139/-64° C
Max working Temp tube side : 40 ° C & shell side : 129° C
Actual working Temp tube side : 25 - 35 ° C & shell side : ≥ 130 < 140 ° C
Issue to be discuss
Every four years and in some cases less than that. We have to replace the top raw of the tube due the size of the defect more than 40%. we have observed discoloration at outer layers of the tubes opposite to the gas inlet nozzle and internally evidence of pits with sing of pink/red discoloration.
The internal corrosion observed is characteristic of Hot spot corrosion ( denickelification). However, this failure occur frequently and we know it, also it has been addressed in many paper such NACE paper No. 599.
My concern as following:
What is the tube outer skin Temp assuming the shell side operate above 130° C and tube side 35 ° C , tube wall 1.626mm ?
Is the tube material suitable for such application knowing that the offset Temp of the process goes beyond the threshold temp of the tube? Despite, its good corrosion resistance to sea water.
Some of the literature address the denickelification occur above 90 ° C. and some of them above 130 ° C. which temperature we should consider during material selection?
Is any fellow face such failure, if so, how it has been mitigated?
Is the water flow contribute in such failure?
thanks in advance
Sea cooling water system provides the main cooling medium for heat removal in to our plant through heat exchangers. The cooler details are as follows.
Fixed tube ASME code, section VIII, Division 1, 1998 Edition and 1999 addenda
Tube material- ASTM B111 C71640
Tube side: seawater / shell side: Natural Gas
Design Temp tube side : 85/-64 °C & shell side : 139/-64° C
Max working Temp tube side : 40 ° C & shell side : 129° C
Actual working Temp tube side : 25 - 35 ° C & shell side : ≥ 130 < 140 ° C
Issue to be discuss
Every four years and in some cases less than that. We have to replace the top raw of the tube due the size of the defect more than 40%. we have observed discoloration at outer layers of the tubes opposite to the gas inlet nozzle and internally evidence of pits with sing of pink/red discoloration.
The internal corrosion observed is characteristic of Hot spot corrosion ( denickelification). However, this failure occur frequently and we know it, also it has been addressed in many paper such NACE paper No. 599.
My concern as following:
What is the tube outer skin Temp assuming the shell side operate above 130° C and tube side 35 ° C , tube wall 1.626mm ?
Is the tube material suitable for such application knowing that the offset Temp of the process goes beyond the threshold temp of the tube? Despite, its good corrosion resistance to sea water.
Some of the literature address the denickelification occur above 90 ° C. and some of them above 130 ° C. which temperature we should consider during material selection?
Is any fellow face such failure, if so, how it has been mitigated?
Is the water flow contribute in such failure?
thanks in advance