I have a 13.8kV 3 phase generator that I'm connecting to the utility as part of a DER project.
So I've been pouring over the interconnection requirements documents from several local utilities and all of them show a transformer between the generator and the utility.
What if my generation is at the same voltage as the utility?
If the utility is 13.8kV, 3 phase, 4 wire connection, and my generation is also 13.8kV, how do I go about determining the grounding requirements for my three phase generator?
Typically I put an NGR on the generator neutral or transformer neutral (depending on configuration) and call it a day.
But if I put a NGR on the generator neutral and I'm connected to 3 phase, 4 wire utility connection, I'm basically bypassing the NGR no since the fault current won't be limited to 5A?
The NGR will still protect my generator, but does it wreck things on the utility side?