davidbeach
Electrical
- Mar 13, 2003
- 9,493
Our distribution system is a pretty normal North American system where the transmission/sub-transmission system feeds the delta winding of the delta-wye transformer(s) in the substations and distribution feeders extend outward as radial load serving, multi-grounded neutral, feeders. Just like they've been for 125+ years.
Now we're facing the situation at some of our rural substations of having enough PV installed that the distribution system could become a source to the transmission system. Obviously any fuse protected transformers will need to get relays and circuit switchers. What's got me a bit puzzled is what to do about lack of a ground reference for the transmission. If I could start from scratch, I'd put wye-delta-wye transformers in the substations but that's impossible now as we have to maintain the existing phasing of that load can be moved seamlessly between substations.
Has anybody else faced this? I can't imagine we're the first. What do you do? Add a grounding transformer? Just change out the arrestors? Ignore it? Something else? Thanks.
Now we're facing the situation at some of our rural substations of having enough PV installed that the distribution system could become a source to the transmission system. Obviously any fuse protected transformers will need to get relays and circuit switchers. What's got me a bit puzzled is what to do about lack of a ground reference for the transmission. If I could start from scratch, I'd put wye-delta-wye transformers in the substations but that's impossible now as we have to maintain the existing phasing of that load can be moved seamlessly between substations.
Has anybody else faced this? I can't imagine we're the first. What do you do? Add a grounding transformer? Just change out the arrestors? Ignore it? Something else? Thanks.