antigfk
Electrical
- Mar 26, 2009
- 33
Hello all,
I have a 2500kVA, 60Hz, 5.75%Z, 480V-wye to 7200V-delta transformer. I will be using a couple of 440V, 50Hz gensets to start and run a customers 6600V, 50Hz, 650HP motor.
I am aware that typically a 60Hz-rated transformer can be derated for 50Hz service by derating the voltage to the ratio of 5/6, or 80%. I however will be running the transformer at 91.6% voltage.
-Is total transformer impedance reduced to 80% of rated, due to 80% rated frequency, because Z=j?L?
-What is the proper method to determine the derated transformer full-load kVA in my situation?
-Normally let-through kVA would be calculated by 2500/0.0575. How would I calculate the let-through kVA in this situation running 50Hz at 91.6% voltage?
Thanks in advance!
I have a 2500kVA, 60Hz, 5.75%Z, 480V-wye to 7200V-delta transformer. I will be using a couple of 440V, 50Hz gensets to start and run a customers 6600V, 50Hz, 650HP motor.
I am aware that typically a 60Hz-rated transformer can be derated for 50Hz service by derating the voltage to the ratio of 5/6, or 80%. I however will be running the transformer at 91.6% voltage.
-Is total transformer impedance reduced to 80% of rated, due to 80% rated frequency, because Z=j?L?
-What is the proper method to determine the derated transformer full-load kVA in my situation?
-Normally let-through kVA would be calculated by 2500/0.0575. How would I calculate the let-through kVA in this situation running 50Hz at 91.6% voltage?
Thanks in advance!