Derating Factors for cables in Cable Trench - IEC Table A.52.3

Status
Not open for further replies.

NickParker

Electrical
Sep 1, 2017
420
Which method of Installation to be followed, which are mentioned in the IEC 60364-5-52 table A.52.3 for consideration of derating factors for cables laid in
1) Concrete cable trench covered with removable concrete slabs.
2) Concrete cable trench covered with removable steel chequered plates.
 
 https://files.engineering.com/getfile.aspx?folder=54f60c4c-6dc1-4978-b1e8-3530f6e95790&file=Table_A.52.3.pdf
Replies continue below

Recommended for you

In my opinion -see Table 52.3[not A52-3] pos. 40 for concrete slabs and 50 or 51 for chequered plates
 
Sorry. I have 2001 edition with me. In 2009 edition A.52.3 is the same as 52.3.
 