Derating SOW Cable

Status
Not open for further replies.

dinkelja

Electrical
Dec 10, 2004
31
Does anyone know, in general what NEC section (table) best describes how to derate SOW type cable. I am unable to verify voltage drop calcs. The application is for (temporary) power disto from smaller portable generators (15kw). The cord reels are specified with 200' SOW cable, 3wire+G #10AWG "split" single phase, 240V. The continuous load is one 1.5 hp 230V motor (10A), and two 750W-120V lights, one per leg. When we say 10A @240V single phase, we mean 10A per wire correct? Ambient 30degC. Just looking for less than 5% on the 230V motor. No electronics so the overall circuit VD doesn't concern me. Would anyone be able to calc if they know? I find about 8.1V with 16.25A load. Say the neutral caried both 750W lights, is it necessary to derate further if it carries a net current? Thanks, JD (EIT).
 
Replies continue below

Recommended for you

I guess I'm okay with the ampacity and voltage drop. I am concerned that we probably will not have all of it off of the reel at once. Meaning that it will have to dissipate whatever fraction x 250W is wound around the reel. Could this prove to be a problem, opinions? Full load operates for about 30 minutes. I think we'll try to get SJOW, 90 deg insulation too.
 