design Anchor force on SLOPE W 2

Status
Not open for further replies.

pelelo

Geotechnical
Aug 10, 2009
357
Hello,

I am analysing an excavation using SLOPE-W.

About 1 m off the top of the 10 m excavation there is a 4 story building.

According to the results i get from Slope W, I need to use any kind of earth retaining system (FS<1) on the excavation in order to make is stable (e.g anchors, nails, etc).

My question is, how could i obtain the design anchor force from SLOPE W? Is there any way to do so? Or will I need to enter several anchor force values until I get the Factor of safety i am looking for?

Please let me know.
 
Replies continue below

Recommended for you

There must be a way in Slope/W. I use Slide and it has an option 'show support forces' to get this data.

On another note, if you use grout anchors in the upper strata, there is a potential that the adjacent building could move up by inches.
 
Be careful using a flexible sheeting system to support a 4 story building. I would not do that. It would probably be more appropriate to use conventional concrete underpinning piers, a secant pile wall, jet grouting, or a slurry wall (in increasing order of cost). Soil nailing is not appropriate for supporting a building, big or small. Soil nail walls require significant open cuts along and below the existing building in order to install the nails and shotcrete. A building can fall down before you drill the first nail or spray the first load of shotcrete. A soil nail wall needs movement to transfer load to the passive nail tendons. Movement means settlement of the building. Building settlement can mean injury, damage, and a lawsuit. A combination of tiedback or braced sheeting with micropiles to support the existing foundations may also be economical.

 
1 m seem too near to slope. it is necessary consololidation before excavation. it is in seismic zone?
 
Thanks for you reply.

We are planning to deal with anchors as due to the site restrictions a small anchor drilling machine will be more accesible than any slurry wall drill rig, or secant piles drill rig.

I don't see very clearly the required anchor force from SLOPE W. I see the free body diagram force from each slice, but no information is given regarding any additional force required to stabilize the slope. Or maybe slope W doesn't show any information at all.

What I think is there should be an easier way instead of assigning an anchor forces and trying to chase the FS you are looking for. Mayeb it would be easier if I try another software, any ideas?

The adjacent building is 1 m off the slope, consolidation is not necessary as the soil profile is silty sand (SM), with n values between 10 and 20.

 
For the few slope stability programs I have seen, you enter in a tieback force, by trial and error, and then see if the safety factor is OK. The programs do not calculate the required tieback force. For a program that calculates the tieback force, you need a wall design program such as CivilTech Software's Shoring Suite. However, the wall programs will not do a global slope stability analysis, as far as I have seen.

 
To add to PEinc's thoughts, why not draw a 10 m excavation with surcharge loading at 1 m distance. Add static earth pressure using Terzaghi/Peck trapezoid + any seismic and water earth pressure?

Chapter 7 of this book covers your topic better than any other book I have read:


Alternatively, you can get SoilStructure.com Lateral Stress Software Program to do this analysis for you.
 
Thanks guys for your inputs.

I will try to get both CivilTech Software's Shoring Suite and
SoilStructure, to see how they work.

Thanks again
 